#1 | | Electrical questions Name: Bas City: Raleigh State: NC County: Wake Join Date: Aug 2007 Age: 36  10-03-2009, 08:46 PM
Senior Administrator One more coat of paint and I can start wiring! A couple of questions:
(1) To wire the fluorescent lights, I plan to run the wire in EMT conduit to a strategically located box on the ceiling, and from there use 3/8" flexible aluminum cable ("fixture whip"). Since I will use the EMT conduit as the ground (vs. running a separate wire), I believe I have to add a ground wire at this point. Does that wire need to have green insulation, or can it be a bare wire?
(2) Does a ceiling box _have_ to be octagonal? I believe it can be square, but I'm having a hard time finding a reference. Side question - what's the advantage of having an octagonal box to begin with?
(3) Is there a place where I can buy 10 gauge solid wire? The BORGs and Ace only sell it stranded? I can order it online, but I only need 50ft.
__________________
Bas.
I don't need it. I just want it.
| | Views: 318 |
10-03-2009, 09:40 PM
|
#2 |
Name: Jack City: Zebulon State: NC County: Wake Join Date: Aug 2009 Age: 69 Avg Visit Freq/Week = 5.62 over 91 days | Re: Electrical questions Square boxes are normally Junction boxes, octagonal boxes normally are fixture boxes because the round bases will cover the oct box. Also there is more room in square for wires to be joined whereas normally to a fixture there is only one or two wires if things are in series. IMHO
For grnd wire bare will do just make it a very solid connection. Stranded wire will work fine, actually better than solid since it is way more flexible. |
| |
10-03-2009, 09:53 PM
|
#3 | | Secretary
Name: Scott Smith City: New Hill State: NC County: Chatham Join Date: Mar 2007 Avg Visit Freq/Week = 6.53 over 180 days | Re: Electrical questions Originally Posted by Bas One more coat of paint and I can start wiring! A couple of questions:
(3) Is there a place where I can buy 10 gauge solid wire? The BORGs and Ace only sell it stranded? I can order it online, but I only need 50ft. Personally I prefer stranded; however the best local place that I know of for electrical supplies is City Electric Supply (CES). They have several local branches; I use the one in Cary. They sell wire by the foot so you only have to buy what you need. |
| |
10-03-2009, 10:19 PM
|
#4 | | President Moderator
Name: Doug Robinson City: Raleigh State: NC County: Wake Join Date: Jul 2006 Age: 48 Avg Visit Freq/Week = 6.96 over 180 days | Re: Electrical questions Bas:
I have a large roll off wire I used to wire my shop. Large grade my electrician friend recommended.
__________________
Doug
Undergoing yet ANOTHER shop reorganization!
|
| |
10-03-2009, 11:12 PM
|
#5 |
Name: Dennis City: Ivan's Corner (Monroe) State: NC County: Union Join Date: Jan 2007 Avg Visit Freq/Week = 6.73 over 180 days | Re: Electrical questions (1) To wire the fluorescent lights, I plan to run the wire in EMT conduit to a strategically located box on the ceiling, and from there use 3/8" flexible aluminum cable ("fixture whip"). Since I will use the EMT conduit as the ground (vs. running a separate wire), I believe I have to add a ground wire at this point. Does that wire need to have green insulation, or can it be a bare wire? The fixture whip, (aka MC cable) if connected properly to the EMT and the fixture, will act as a grounding device. No other grounding is required beyond this method provided the EMT is connected properly from the panel box to the fixture or device.
As for switches & receptacles, you will need to use a grounding screw & pigtail (green wire) to the device. These are available ready to go from the BORGs.
__________________
WHAT BOX?
|
| |
10-04-2009, 11:02 AM
|
#6 | | Senior Administrator
Name: Bas City: Raleigh State: NC County: Wake Join Date: Aug 2007 Age: 36 Avg Visit Freq/Week = 6.96 over 180 days | Re: Electrical questions Originally Posted by Skymaster Stranded wire will work fine, actually better than solid since it is way more flexible. I only have to go 20 feet or so, with one 90 at the end, so in my case flexibility isn't that important. But yeah, I looked at some 10 gauge solid wire and that stuff is tough...I would not want to pull that around 3 or 4 bends. Originally Posted by scsmith42 Personally I prefer stranded; however the best local place that I know of for electrical supplies is City Electric Supply (CES). They have several local branches; I use the one in Cary. They sell wire by the foot so you only have to buy what you need. Thanks Scott! Originally Posted by Douglas Robinson I have a large roll off wire I used to wire my shop. Large grade my electrician friend recommended. Expect a PM coming your way. I've been meaning to come check out your shop and ooh and aah over your J/P, now I really I need to get my behind in gear! Originally Posted by Gotcha6 The fixture whip, (aka MC cable) if connected properly to the EMT and the fixture, will act as a grounding device. No other grounding is required beyond this method provided the EMT is connected properly from the panel box to the fixture or device.
As for switches & receptacles, you will need to use a grounding screw & pigtail (green wire) to the device. These are available ready to go from the BORGs. That makes sense Dennis. To clarify, I'm making my own fixture whip using the MC cable and wire. The premade armored cable I saw at the BORG had a separate ground wire, which is why I assumed that was needed. But that's probably because some people will connect it to PVC (NMT).
I think I have every connector, screw, cover plate, strap and fitting I need at this point
BTW, I saw something at Home Depot I had not seen before, grounding clips. You stick the ground wire in the clip, then slide the clip over the box wall. No screw. I suppose the cover plate will hold the clip in place, but I've never seen a box wired that way before.
Thanks for the help everyone.
__________________
Bas.
I don't need it. I just want it.
|
| |
10-04-2009, 12:21 PM
|
#7 |
Name: Jack City: Zebulon State: NC County: Wake Join Date: Aug 2009 Age: 69 Avg Visit Freq/Week = 5.62 over 91 days | Re: Electrical questions Bas; tension and friction hold those grounding clips to the side of the box. I am not an electrician but have done a bit and I never got comfortable with them. I believe in a really tight connection either wire nutted or to a grounding screw, I dont like loose grounds :}:}  |
| |
10-04-2009, 03:16 PM
|
#8 |
Name: Dave City: Raleigh State: NC County: Wake Join Date: Jul 2005 Avg Visit Freq/Week = 6.26 over 180 days | Re: Electrical questions For the #10 solid you can go buy it in romex/nm form and just strip off the outer cover |
| |
10-04-2009, 04:44 PM
|
#9 |
Name: Jeff City: Apex State: NC County: Wake Join Date: May 2007 Avg Visit Freq/Week = 4.59 over 180 days | Re: Electrical questions You must have some big equipment. 10 gauge will do 30 amps or enough to do a electric stove. I'm curious as to what you are running on the circuit.
Jeff |
| |
10-04-2009, 10:56 PM
|
#10 | | Senior Administrator
Name: Bas City: Raleigh State: NC County: Wake Join Date: Aug 2007 Age: 36 Avg Visit Freq/Week = 6.96 over 180 days | Re: Electrical questions Originally Posted by Skymaster I believe in a really tight connection either wire nutted or to a grounding screw, I dont like loose grounds :}:}  Same here. They were marked down from $7 to $2 for 100, but even at that price I just couldn't see myself securing the ground wire. I've never had a connection come loose (knock on wood) and I'm not about to start either! Originally Posted by jlwest You must have some big equipment. 10 gauge will do 30 amps or enough to do a electric stove. I'm curious as to what you are running on the circuit. Well, so far - nothing  ! But I'm looking to upgrade pretty soon. One of the items I'm considering is the G0441 dust collector, which draws 22 amps @ 240V. The rest of the equipment should run just fine on 20A circuits, but you never know what you run across. This will save me some time rewiring if I do need 5HP, all I'd have to do is swap out the breaker.
__________________
Bas.
I don't need it. I just want it.
|
| |
10-05-2009, 09:10 AM
|
#11 |
Name: Jeff City: Apex State: NC County: Wake Join Date: May 2007 Avg Visit Freq/Week = 4.59 over 180 days | Re: Electrical questions That is a lot of amps at 240v. Grizzly has traditionally used Chinese motors which are notorious power hogs because of the cheap copper they use in the windings. That will be one nice dust collection system. Did you check out Onieda? Probably more initial cost but cheaper operational cost.
Jeff  |
| |
10-05-2009, 06:25 PM
|
#12 |
Name: James City: Apex State: NC County: Wake Join Date: Aug 2009 Avg Visit Freq/Week = 0.91 over 92 days | Re: Electrical questions Originally Posted by Bas One of the items I'm considering is the G0441 dust collector, which draws 22 amps @ 240V.  That's a heck of a lot of power for a "3HP" dust collector. 22A @ 220V = 6.5HP!
__________________
I've cut this board 3 times and it's still too short.
|
| |
10-06-2009, 01:33 PM
|
#13 | | Executive Vice-President Libraries Administrator
Name: Rob City: Hendersonville State: NC County: Henderson Join Date: Nov 2005 Age: 67 Avg Visit Freq/Week = 6.88 over 180 days | Re: Electrical questions A ClearVue CV1800 Cyclone is equipped with a Leeson 5 HP motor that draws 20.8 Full Load Amps. I'm using #10 wire on a 30 Amp breaker and a 30 Amp contactor for the on/off control for mine.
__________________
Rob Payne  Truths: There is no such thing as a 25 hour day, so why do I keep trying to cram so much into every day so it seems that way! |
| |  | | Thread Tools | | | | Display Modes | Linear Mode |
Posting Rules
| You may not post new threads You may not post replies You may not post attachments You may not edit your posts HTML code is Off | | |
Similar Threads | | Thread | Thread Starter | Forum | Replies | Last Post | | Electrical help | Travis Porter | Power Tools and Their Use | 12 | 08-29-2008 09:35 PM | | » Stats |
Members: 3,665
Threads: 25,109
Posts: 263,786
Top Poster: DaveO (14,702) | | Welcome to our newest member, wmdale | |